A factory has an electrical load of 1600 kW at a lagging power factor of 0.8. An additional variable power factor load is to be

added to the factory. The new load will add 320 kW to the factory. The power factor of the variable power factor load is to be adjusted so that the overall power factor of the factory is 0.96 lagging.a) What is the reactive power associated with the added load?b) Does that load absorb or deliver magnetising vars (reactive power is also sometime referred to as magnetising vars. Inductors absorb magnetising vars and capacitors deliver magnetising vars)c) What is the power factor of the adjustable power factor load?d) If the voltage at the input is 2400 V(rms), what is the magnitude of the current into the factory before the adjustable load?e) What is the magnitude of the current with the adjustable load?
Engineering
1 answer:
Liono4ka [1.6K]2 years ago
8 0

Answer:

Explanation:

a)

Apparent power|S0| of the original load:

|S0|=P0/0.8=1600000/0.8

|S0|=2000kvA

P0 is the average power of the original load.

To determine the relative power Q0 of the original load :

Q0=√|S0|^2-P0^2

=√(2000000^2)-(1600000)^2=1200kVAR

Complex power of the original load S0:

S0=P0+jQ0

=1600+j1200kvA

After the additional power factor load, the final power Pf is :

Pf=1600000+320000=1920kw

Therefore the final apparent power |Sf| of the load will be:

|Sf |=Pf/0.96

|Sf|=1920000/0.96=2000kvA

Hence, the reactive power (Qf) of the composite Load:

Qf=√|Sf|^2-P^2

Qf=√(2000000)^2-(1920000)^2=560kVAR

Now, the final complex power(Sf) associated with the composite load is:

Q(add)=Qf-Q0

Q(add)=560000-1200000

=-640kVAR

b) Yes, since the reactive power value of the added load is negative, the added load delivers magnetizing vars:

c) Complex power S(add) of the added load:

S(add)=P(add) + jQ(add)

S(add)=320000-j640000

S(add)=715541.753<-63.435

The phase difference between the added load voltage and current is:

Qv-Qi=-63.435

The power factor Pf of the added load :

Pf=cos(-63.435)=0.447

Therefore, the added load current leads the voltage, the power of the additional load or adjustable power factor is leading by:

Pf=0.447leading

d) the current into the factory (I) before adding the power factor load is:

I=S0/2400

I=1600000-j1200000/2400

I=666.667-j500

I=833.33<-36.87A(rms)

rms magnitude of the current into the factory| I| before adding the power factor load is given as:

|I|=833.33A(rms)

e) current into the factory ,I, after adding the power factor load :

I=Sf*/2400

I=1920000-j560000/2400

I=833.33<-16.25•(rms)

Therefore, rms magnitude of the current into the factory |I| after adding the power factor load is :

|I|=833.33A(rms)

Finally ,adding the capacitor has not changed the current rms magnitude but it's phase only.

You might be interested in
A tank contains 500 kg of a liquid whose specific gravity is 2. Determine the volume of the liquid in the tank.
horsena [70]

Answer:

So\ the\ volume\ of\ liquid\ = 0.25\ m^3

Explanation:

given that

Mass m = 500 kg

Specific gravity = 2

So\ density\ of\ liquid\ =2000 \frac{kg}{m^3}

We know that

mass = density x volume

So by putting the values

mass = density x volume

500 = 2000 x volume

So\ the\ volume\ of\ liquid\ = 0.25\ m^3

4 0
2 years ago
You are an electrician on the job. The electrical blueprint shows that eight 500-W lamps are to be installed on the same circuit
Alchen [17]

Answer:

I = 14.44A

Explanation:

calculating 80% of the circuit breaker current

I = (80/100)20A = 16A

eight 500W lamps are to be installed on the circuit. assume they are connected in parallel

total power = 500 x 8 = 4000W

power = voltage x current

current = power/voltage = 4000W/277V = 14.4A

The current obtained is less than 80% of the circuit breaker.

20A circuit breaker is large enough to carry the load.

3 0
2 years ago
A solar radiation flux of 700 W/m2 is absorbed in a metal plate that is perfectly insulated on the back surface. The convection
skad [1K]

Answer:

The main solution to this problem is to note that under equilibrium conditions, the rate at which heat is transferred into the metal plate from the sun by radiation must be equal to the rate at which heat is lost from the plate to the surrounding air by convection.

Explanation:

Therefore, qᵃ = qᵇΔT

where

a = Radiation energy source

b = Convection energy source

ΔT = Tp - Ta = Temperature change between the plate and the air under equilibrium condition

Given,

qᵃ = 700 W/m2

qᵇ = 10 W/m2K - 100 W/m2K

Hence, for qᵇ = 10 W/m2K,

        ΔT = qᵃ / qᵇ

        ΔT = 700/10 = 70K

Similarly, for qᵇ = 100 W/m2K

              ΔT = 700/100 = 7K

The temperature change of the plate under equilibrium conditions range from 7K to 70K.

4 0
2 years ago
A rectifier charges a battery bank in a substation. The bank rated dc voltage is 48 V. The required charging current is 25 A. Th
Vsevolod [243]

Answer:

See explaination

Explanation:

A constant voltage source is called a DC Voltage with a voltage that varies periodically with time is called an AC voltage. Voltage is measured in volts, with one volt being defined as the electrical pressure required to force an electrical current of one ampere through a resistance of one Ohm.

Please check the attached file.

7 0
2 years ago
The velocity distribution for laminar flow between parallel plates is given by u umax = 1 − ( 2y h ) 2 Where h is the distance s
Lynna [10]

Answer:

Explanation:

For we to calculate the shear stress on the upper plate and give its direction. Sketch the variation of shear stress across the channel, I used hand in solving it, check attached file below

5 0
2 years ago
Other questions:
  • a. Replacing standard incandescent lightbulbs with energy-efficient compact fluorescent lightbulbs can save a lot of energy. Cal
    9·1 answer
  • 1. Technician A says that an automotive
    8·1 answer
  • A 12-L volume of oil is subjected to a pressure change, which produces a volume strain on the oil of -3.0 × 10-4. The bulk modu
    6·1 answer
  • An excited electron in an Na atom emits radiation at a wavelength 589 nm and returns to the ground state. If the mean time for t
    10·1 answer
  • The 10-kg block slides down 2 m on the rough surface with kinetic friction coefficient μk = 0.2. What is the work done by the fr
    7·1 answer
  • 3–102 One of the common procedures in fitness programs is to determine the fat-to-muscle ratio of the body. This is based on the
    5·1 answer
  • When tires are underinflated, it leads to ______.
    10·2 answers
  • R-134a vapor enters into a turbine at 250 psia and 175°F. The temperature of R-134a is reduced to 20°F in this turbine while its
    11·1 answer
  • A cylindrical rod 100 mm long and having a diameter of 10.0 mm is to be deformed using a tensile load of 27,500 N. It must not e
    6·1 answer
  • Marty is developing a new way to heat an airplane's windshield to prevent it from accumulating ice when in flight. A thin layer
    9·1 answer
Add answer
Login
Not registered? Fast signup
Signup
Login Signup
Ask question!